The next releases will be DM Electrical RT 1.4, DM Electrical 8.6, DM HVAC 7.4, and DM Plumbing 4.2 We are actively working on these release and using this wishlist to guide which features we implement. Some features you see marked as “complete” will not be available until these releases are finished.

  • Hot ideas
  • Top ideas
  • New ideas
  • My feedback
  1. Default elevations for all electrical devices

    You can specific a default elevation for light fixtures in the schedule. Expand this functionality to all types of electrical devices.

    2 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  2. Unique ID for all Feeders and Branch Circuits

    Have a way to make a unique cable ID for every feeder, branch circuit and low voltage circuit. For example P-MCC1-001 for the power cable fed from MCC1 or PT-FLOWGAS-003 for a pressure transmitter.

    I'm working on a big industrial plant where I need a have a cable number for every cable in the plant.

    I would like to have the ID on the one line, plan view drawing and export to Excel.

    10 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    high effort to implement  ·  1 comment  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  3. Add a "match circuit" command.

    Make the "Select Circuit from Drawing <" button a command that can be typed into the command line. After this command has been run, do not show the Circuiting window, instead go immediately to "Circuit Devices <". The user can then continue to circuit additional devices to the circuit they selected. A double right click would bring up the Circuiting window or the user could escape out of the command without showing the window.

    32 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    low effort to implement  ·  3 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  4. Upsize Wires Based upon Voltage Drop

    Automatically upsize branch circuit wires when necessary because of voltage drop.

    151 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  4 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  5. Count devices connected to recurring panels

    Have schedule quantities and takeoffs count the number of items connected to recurring panels.

    2 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  1 comment  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  6. SKM Power Tools

    Provide the ability to import and export panel schedules and switchboard schedules between Design Master and SKM PowerTools for Windows.

    15 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    high effort to implement  ·  5 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  7. Use commas or spaces to separate voltage, #poles, #wires ect for equipment callouts

    Currently information on the equipment call out is all grouped together without separation. We have had this requested several times by our clients who would like this changed on our drawings. To currently meet this request we are spending to much time adjusting these individually.

    1 vote
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    low effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  8. Locate and edit schedules within groups to create T.I. voltage drop and other schedules that don't include the entire project.

    When there is T.I. work within a large project you want to show only the the voltage drop for the TI space. You have to deselect all the equipment not in the space one at a time to show a voltage drop schedule for just the TI work. What if you could group the panels in a similar way to luminaires so that the TI voltage drop or fault schedule has only the TI panels, without disabling the ability to show a schedule for the main project or another TI within that project.

    3 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  9. Arc-flash label sizes

    Be able to change the size of the arc-flash labels to fit a specific size.

    7 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  10. Swap & Copy Circuits

    When copying circuits in the swap and copy dialog, multipole breakers do not copy to the new location as multipole breakers, they copy as single pole. It appears that you have to set the number of poles and their positions in the circuiting dialog before starting the copy/swap routine.

    47 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    low effort to implement  ·  6 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  11. Do "Amps by Phase" using calculated loads on high-leg delta panels

    High-leg delta panels are always unbalanced. The balanced 3-phase amps we display is not a good number to use when sizing these panels. The connected amps by phase does not account for largest motor loads or continuous loads.

    Add the ability to determine the amps by phase using calculated loads. The largest motor, lighting, and continuous loads would all be calculated at 125%. All other loads would be calculated at 100%.

    12 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  12. Redundant Ground

    Add "Redundant Ground" as an option for receptacles. Would add an additional ground wire to the tick marks and add an "RG" or similar label to the receptacle itself.

    10 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    low effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  13. Tick marks for more than 1-pole, wire callouts for > #12

    Add another option to "Homerun wire callouts and tick marks" labeled "Tick marks for more than 1-pole , wire callouts for > #12".

    3 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  1 comment  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  14. Improve Indoor Lighting Level Report

    Add "Allowed Watts / SF" as a field to rooms.

    Add "Allowed Watts / SF" and "Total Allowed Watts" as columns to the indoor lighting schedule.

    Add a "Totals" row at the bottom that totals the area, allowed watts, and computed watts.

    3 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  15. Draw Circuit Loops Using Polylines instead of Arcs

    When you loop from one device to another, be able to select that loop and break it in to two loops that can each individually be moved or broke. This way we can have "S" loops.

    DM Note: When we implement this, it will probably be by allowing you to insert a loop using a pline. This will allow you to insert the loop however you want without any restrictions.

    31 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  7 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  16. 4 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  17. Photometric calculation schedule

    I would like to suggest that the photometric calculation schedule be a combined schedule for all rooms instead of a dedicated schedule for each single room/space (or both options be available). We are typically asked to provide a single schedule that lists the room/space name in the first column and then the various footcandle columns.

    3 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    medium effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  18. A spreadsheet like table, simular to the fault calculations, that shows all the load calculation fields by panel, as they move to the final

    A spreadsheet like table, similar to the fault calculations, that shows all the load calculation categories by panel, as they move to the final service calculation. We could then turn the load calculation footer off on the panel schedules and include this summary table in the drawings. It would also be great to figure out how the loads are adding up.

    6 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    high effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  19. Insert Devices via command line

    Be able to insert a receptacle/device without picking it from the 'Insert Receptacle' form. A command followed by the device name would prompt the user to place the receptacle like they just clicked "OK" after selecting a device.

    4 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    high effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  20. Multi text search

    implement Multi-Text search through out the menus.

    So for example when searching through the Insert Receptacle menu and in my case we have several thousand pieces of equipment. if the equipment is called 'RX99S' instead of just allowing us to hit 'R' and starting us off at the beginning of the list of 'R' equipment allow us to type out 'RX99S' and design master go straight to the piece of equipment. this is a very simple change to the code in design master and would save tons of time on projects.

    20 votes
    Vote
    Sign in
    (thinking…)
    Sign in with: Facebook Google
    Signed in as (Sign out)
    You have left! (?) (thinking…)
    high effort to implement  ·  0 comments  ·  Electrical  ·  Flag idea as inappropriate…  ·  Admin →
  • Don't see your idea?

Design Master Wish List

Categories

Feedback and Knowledge Base