The current releases are DM Electrical RT 1.1, DM Electrical 8.4, DM HVAC 7.3, and DM Plumbing 4.1. We are not adding new features to these releases.

The next releases will be DM Electrical RT 1.2, DM Electrical 8.5, DM HVAC 7.4, and DM Plumbing 4.2 We are actively working on these release and using this wishlist to guide which features we implement. Some features you see marked as “complete” will not be available until these releases are finished.

How can we improve Design Master?

You've used all your votes and won't be able to post a new idea, but you can still search and comment on existing ideas.

There are two ways to get more votes:

  • When an admin closes an idea you've voted on, you'll get your votes back from that idea.
  • You can remove your votes from an open idea you support.
  • To see ideas you have already voted on, select the "My feedback" filter and select "My open ideas".
(thinking…)

Enter your idea and we'll search to see if someone has already suggested it.

If a similar idea already exists, you can support and comment on it.

If it doesn't exist, you can post your idea so others can support it.

Enter your idea and we'll search to see if someone has already suggested it.

  • Hot ideas
  • Top ideas
  • New ideas
  • My feedback
  1. Spaces in Feeder Callouts

    Be able to display feeder callouts with spaces after commas, instead of having all the wire sizes right next to each other.

    Current Callout:
    2''C,2#3/0,#3/0N,#6G

    Desired Callout:
    2''C, 2#3/0, #3/0N, #6G

    3 votes
    Vote
    Sign in
    Check!
    (thinking…)
    Reset
    or sign in with
    • facebook
    • google
      Password icon
      Signed in as (Sign out)
      You have left! (?) (thinking…)
    • Manufacturer Name field included within Notes Settings of distribution equipment

      It would be helpful when creating distribution equipment lists if there was an option for the manufacturer's name. Currently we have to use an unused Note key, rename the label for that key and then remember which Notes Setting corresponds to the list entry.

      3 votes
      Vote
      Sign in
      Check!
      (thinking…)
      Reset
      or sign in with
      • facebook
      • google
        Password icon
        Signed in as (Sign out)
        You have left! (?) (thinking…)
      • Erase Note - multiple

        Select multiple devices and delete all custom notes (not fixture callouts) attached to them.
        The "Match Device Label Locations" command can add many callouts at once, but there does not seem to be a way to easily delete multiple callouts.
        This would be especially useful when adding lights to a circuit that already contains lights. Running “Draw Homerun And Loops" would erase a lot of my work, so I usually delete all the circuit callouts manually before drawing loops manually.
        If this feature already exists, please make it easier to find.

        3 votes
        Vote
        Sign in
        Check!
        (thinking…)
        Reset
        or sign in with
        • facebook
        • google
          Password icon
          Signed in as (Sign out)
          You have left! (?) (thinking…)
        • Paralleling Switchgear Support

          Would be very helpful to be able to be able to have multiple sources connect to the same bus. We have had numerous situations where we have had Geneva type switches, multiple kirk-key input as well as paralleling switchgear situations where we were unable to find a "work-around" using this software. This is becoming especially common with ConEdison now permitting the paralleling of electrical sources.

          3 votes
          Vote
          Sign in
          Check!
          (thinking…)
          Reset
          or sign in with
          • facebook
          • google
            Password icon
            Signed in as (Sign out)
            You have left! (?) (thinking…)
          • Multiple Fault Schedules

            I would like the ability to break out individual fault current schedule entries into separate groups based on the service connection or other arbitrary criteria. For example, in a project with three electrical services, the distribution equipment fault current associated with one service could be scheduled separately from the other two services. Design Master currently schedules all fault current schedule entries together. On projects with multiple services and dozens of distribution equipment entries, a method of showing specific fault current calculations in separate schedules would be invaluable.

            3 votes
            Vote
            Sign in
            Check!
            (thinking…)
            Reset
            or sign in with
            • facebook
            • google
              Password icon
              Signed in as (Sign out)
              You have left! (?) (thinking…)
            • A copy function for identical floor plans in multi-level buildings would be a time saving idea to speed up drawing.

              So that when I am working on a multilevel building all I would have to do is copy the floor plan from one identical level and placing it on the other matching levels then just rename the panels and circuit names, without duplicating the copied information on the original panels. Breaking its connection with the parent panel and giving a notification to reassign panel names.

              4 votes
              Vote
              Sign in
              Check!
              (thinking…)
              Reset
              or sign in with
              • facebook
              • google
                Password icon
                Signed in as (Sign out)
                You have left! (?) (thinking…)
              • Better default panel clearances

                Have better default values for panel clearances, including options to have it vary upon the panel defition.

                1 vote
                Vote
                Sign in
                Check!
                (thinking…)
                Reset
                or sign in with
                • facebook
                • google
                  Password icon
                  Signed in as (Sign out)
                  You have left! (?) (thinking…)
                • Add a hatch pattern to room definitions

                  When defining rooms, it is often difficult to determine which rooms have been defined and which have not, if an area gets surrounded. Adding a hatch pattern on its own layer would make it much easier to determine if you've included all room definition areas.

                  4 votes
                  Vote
                  Sign in
                  Check!
                  (thinking…)
                  Reset
                  or sign in with
                  • facebook
                  • google
                    Password icon
                    Signed in as (Sign out)
                    You have left! (?) (thinking…)
                  • Separate column in the feeder schedule for the service grounding electrode conductor.

                    The service ground does not get installed in the conduit with the service entrance conductors, so why is it shown just like all the other feeders where the equipment grounding conductor is installed with the feeder conductors. If you want the feature to show the GEC size, show it in a different column and show the feeder with no ground listed with the feeder conductors so its clear it is not in the conduit.

                    4 votes
                    Vote
                    Sign in
                    Check!
                    (thinking…)
                    Reset
                    or sign in with
                    • facebook
                    • google
                      Password icon
                      Signed in as (Sign out)
                      You have left! (?) (thinking…)
                    • Improve combined homeruns

                      Be able to combine homeruns with different wire sizes.

                      Be able to combine homeruns from separate panels.

                      Be able to display a full wire callout for combined circuit homeruns, including calculating the conduit size required for all the wires.

                      28 votes
                      Vote
                      Sign in
                      Check!
                      (thinking…)
                      Reset
                      or sign in with
                      • facebook
                      • google
                        Password icon
                        Signed in as (Sign out)
                        You have left! (?) (thinking…)
                      • Voltage Drop Based upon Connected or Other Load

                        Be able to specify that the voltage drop on a feeder should be based upon the connected or other load, rather than the calculated load.

                        One example of a use for this feature is a piece of equipment that serves a single motor. You want the voltage drop for the connected load of the motor, rather than the calculate load, which will be 125% of the motor load.

                        10 votes
                        Vote
                        Sign in
                        Check!
                        (thinking…)
                        Reset
                        or sign in with
                        • facebook
                        • google
                          Password icon
                          Signed in as (Sign out)
                          You have left! (?) (thinking…)
                        • Label homeruns with feeder IDs

                          Label homeruns using feeder IDs like those used in the one-line diagram instead of full text wire callouts.

                          4 votes
                          Vote
                          Sign in
                          Check!
                          (thinking…)
                          Reset
                          or sign in with
                          • facebook
                          • google
                            Password icon
                            Signed in as (Sign out)
                            You have left! (?) (thinking…)
                          • Reset panel "Fixed Loads".

                            Often, I need to "start over" on a panel that I've assigned fixed loads. It would be handy to have a button that would clear every fixed load on the panel. Or even be able to select several circuits and clear those circuit's fixed loads.

                            8 votes
                            Vote
                            Sign in
                            Check!
                            (thinking…)
                            Reset
                            or sign in with
                            • facebook
                            • google
                              Password icon
                              Signed in as (Sign out)
                              You have left! (?) (thinking…)
                            • Subfeed breakers

                              Add specific support for subfeed breakers.

                              Be able to set the number of subfeed breakers on a panel (similar to how the number of poles is currently set on a panel).

                              Have the panel schedule update to document which breakers are subfeed. We likely would add a separator block between the branch circuit and subfeed breakers that you could customize. The default block would have a line across the schedule plus some text indicating branch circuit breakers above and subfeed below. You could then modify that as desired for your documentation purposes.

                              34 votes
                              Vote
                              Sign in
                              Check!
                              (thinking…)
                              Reset
                              or sign in with
                              • facebook
                              • google
                                Password icon
                                Signed in as (Sign out)
                                You have left! (?) (thinking…)
                              • On a one-line diagram, a vertical bus panel should have horizontal branch breakers--NOT vertical!

                                When you generate a one-line diagram, if you have panels that have a vertical bus, their branch breakers end up at the bottom of the bus and are vertical. The look like main breakers--not branch breakers. A work around for this is for every vertical bus panel, generate a riser diagram starting with that panel. Even this work around is not perfect, as you have to resize the vertical bus and fiddle with the branch breaker.

                                7 votes
                                Vote
                                Sign in
                                Check!
                                (thinking…)
                                Reset
                                or sign in with
                                • facebook
                                • google
                                  Password icon
                                  Signed in as (Sign out)
                                  You have left! (?) (thinking…)
                                • Copy panel and loads to new project

                                  Be able to copy panels and other distribution from one project to another. The loads on the panel will be created as fixed loads in the new project.

                                  1 vote
                                  Vote
                                  Sign in
                                  Check!
                                  (thinking…)
                                  Reset
                                  or sign in with
                                  • facebook
                                  • google
                                    Password icon
                                    Signed in as (Sign out)
                                    You have left! (?) (thinking…)
                                  • Show schedule notes on last column when schedule is split

                                    Currently if a schedule has a "Maximum Schedule Height" set the schedule notes are placed at the bottom of the first column. It would be better to place them at the bottom of the last column (or at least have an option to place them there) since the last column is often shorter than the others.

                                    1 vote
                                    Vote
                                    Sign in
                                    Check!
                                    (thinking…)
                                    Reset
                                    or sign in with
                                    • facebook
                                    • google
                                      Password icon
                                      Signed in as (Sign out)
                                      You have left! (?) (thinking…)
                                    • Equipment Panel Description

                                      In the Panel Description dropdown, add "Equipment Callout + Description" to the list, in addition to "Same as Equipment Callout" and "Custom".

                                      1 vote
                                      Vote
                                      Sign in
                                      Check!
                                      (thinking…)
                                      Reset
                                      or sign in with
                                      • facebook
                                      • google
                                        Password icon
                                        Signed in as (Sign out)
                                        You have left! (?) (thinking…)
                                      • Low-voltage looping

                                        Be able to draw loops between devices for low-voltage lines, for connecting items like sensors and power packs.

                                        12 votes
                                        Vote
                                        Sign in
                                        Check!
                                        (thinking…)
                                        Reset
                                        or sign in with
                                        • facebook
                                        • google
                                          Password icon
                                          Signed in as (Sign out)
                                          You have left! (?) (thinking…)
                                        • Default Groups

                                          Have the ability to define a default device group name. In multi-phase projects it would be helpful to be able to set a group name as the default instead of having DM go to the "General" group.

                                          3 votes
                                          Vote
                                          Sign in
                                          Check!
                                          (thinking…)
                                          Reset
                                          or sign in with
                                          • facebook
                                          • google
                                            Password icon
                                            Signed in as (Sign out)
                                            You have left! (?) (thinking…)
                                          ← Previous 1 3 4 5 9 10